Outdated fuse box query
Hi there.
After our father passed away we have his house on the market. The electrics have been given a low score due to having an old fuse box. There has never been any issues with the electrics in the house and I understand that it needs updating. Do you think it possible to have an electrician providing a safety certificate even with this old box, or even to provide a report of assurance that there is no rewire required and the cost of fitting a new fuse system. Unfortunately we don't have funds for a rewire. And we feel this may be putting off buyers as the way it is perceived on the report is that it's a massive concern. We aren't sure what would be involved. It's possible we could update the fuse box but a rewire would be too expensive for us.
Advice from 30 local tradespeople
They can give you a certificate (EICR) but there is a potential it would be unsatisfactory
Hi
i understand you situation about the finances for this work but in this occasion is something that need to be done properly and in accordance with regulations , we have to do a new fuse box with the necessary protection of RCD thats something that we must do ,and if the wire is to old and in the inspection and testing that is done are showing problem will need to be rewired
thank you Ervis
I would recommend an EICR of the property to establish if the existing installation is in good condition. I will however suggest that if the consumer unit is dated and has no suitable protection that meets current requirements and especially if selling the property then it would be advisable to replace said consumer unit after a full inspection has been conducted. Available for any questions if needed.
I don’t think any electrician would give you a satisfactory report as it’s their name is on the certificate to say it’s safe or not and why
The consumer unit has to have RCD protection for all circuits in the property and also a surge protection device fitted in the consumer unit
You also have to make sure the main water supply is bonded and also the gas if there’s any in the property also the wiring in the house should be tested to make sure it’s safe to replace the consumer unit and that nothing will be tripping when installed
Yes
The house would benefit from having and eicr (electrical installation condition report)
This would test all cables and fixtures to allow to give a good report on what I would advise to do next.
Hi
Yes u can get an EICR completed by a qualified electrician and they will do a complete check on your property.
The fusebox is not to current regulations so would be fail on the eicr also it can be changed to a new fusebox
An EICR would be your best bet this will give you a report of the current condition of the Electrical installation
If the wiring was tested with the sufficient passing readings required updating the fuse box would be good enough until such time an upgrade of the house wiring was affordable and immediately required
You need to have the house electrical systems accessed, inspected and tested by a 2391 inspection and testing qualified electrician and adhere to his/her recommendations
Hi there. It's understandable that an old fuse box might raise concerns for potential buyers. While it's possible to obtain a safety certificate for the existing electrical system, it would depend on the overall condition of the wiring and whether it meets current safety standards. An electrician can conduct an Electrical Installation Condition Report (EICR) to assess the system's safety and provide recommendations.
If the fuse box is outdated but still functional, updating it without a full rewire might be a feasible solution. This update can improve safety and potentially ease buyer concerns. However, ensure you consult with a certified electrician to get a precise evaluation and cost estimate. Investing in a new fuse box could make your property more attractive to buyers, but it's essential to weigh the costs and benefits carefully.
An old fuse box does not automatically mean a rewire is needed. A qualified electrician can carry out an EICR to assess the condition of the wiring and advise whether only a consumer unit upgrade is required.
In many cases, the wiring is satisfactory and a full rewire is not necessary.
In the UK an electrician can’t just “issue a safety certificate” to bless an installation with an old fuse box; what they can do is an EICR (Electrical Installation Condition Report), which is the recognised document buyers/agents understand. An old rewireable?fuse board often gets marked down (commonly for lack of RCD protection and modern enclosure), but that doesn’t automatically mean the house needs a full rewire: if testing results are acceptable (earth loop impedance, insulation resistance, bonding present, etc.) it may be coded C3 (improvement recommended) and still be “Satisfactory” overall, or it may be “Unsatisfactory” if there are C1/C2/FI items that need fixing. So yes, it’s possible to have a report that reassures buyers no rewire is indicated, but only if the test results support that; no electrician can honestly guarantee “no rewire required” without doing the inspection and full set of tests. If funds are limited, the usual sensible route is: get an EICR, fix any C1/C2/FI issues, and if the main negative is the old fuse box/lack of RCDs then a consumer unit replacement (plus any remedial bonding/earthing upgrades found) is often far cheaper than a rewire and can significantly improve the report—your electrician can also provide a written quotation for the CU change to show buyers. If you share what the current report actually says (codes and observations) and roughly the age/type of wiring (PVC/T+E vs old rubber/lead), I can tell you whether it sounds like “CU upgrade likely” or “rewire more likely.”
Yes, you can get an EICR (safety certificate) with the old fuse box – but it’ll have a low score until the distribution unit is upgraded. (If required )
• An electrician can inspect the wiring and confirm if a full rewire is not needed (which will reassure buyers).
• Upgrading the fuse box takes 2-6hours and costs £450-£1250 – way cheaper than a rewire.
Would need a new consumer unit at the least.
Would need testing to check wiring
Well firstly , i would do a certificate . If the consumer board is showing signs of hazards , or something that can lead to a hazard , it could get a fail , meaning the board would have to get replaced or a remedial needing done . Rewire would only be needed if the full property the wiring has gone unstable
Yes after a full eicr as been carried out, and depending on the circumstances
Supplementary bonding is all good amd unplaced you could be fine it does after pass readings and so on but90% of the time a new consumer unit fully rcbo can be installed without a rewire been needed again there is other factors to consider but I'm saying yes
It is possible an EICR test will need to be conducted to get a correct report of failures or issues and a report will be concluded with reccomendations.
Yes is possible, but a competent electrician would need to check the wiring of the house to make sure is good conditions.
Hi there,
What do you mean by "a low score"?
The proper way to assess your electrics would be to have an EICR (Electrical Installation Condition Report) carried out. The outcome would be satisfactory or unsatisfactory, with supporting documents and evidence.
Old wiring and fuseboxes / consumer units are not necessarily unsafe (so long as they were compliant with the relevant edition of the wiring regulations at the time of install), but only an electrical inspection and testing procedure can determine their current condition.
I therefore advise you get an EICR done at your property
Hello,
First of all, please accept our condolences in what is no doubt a difficult time.
An electrician can carry out an Electrical Installation Condition Report (EICR) to assess the safety of the electrical system. While the installation may pass, it is likely to receive a C3 advisory code, indicating that it doesn’t meet current standards and that an update is recommended.
However, it’s worth considering whether this approach is the best financial decision. Buyers may use the outdated electrics as leverage to negotiate a lower sale price, especially if the EICR includes recommendations for updating.
You may find it more beneficial to update the electrical installation before the sale, as the electrician is legally required to certify the safety of the new installation upon completion. This would avoid paying for an EICR (often over £150 depending on the property size and location) only to later decide to upgrade the system, or risk losing value in the sale price due to outdated electrics.
Gerrard’s Electrical Solutions is a friendly and reliable company serving the North West, and North Wales. If you’re in our area, we’d be happy to offer a free quotation.
Yes if the wiring condition is good then updating the fuse box will be sufficient to be certified and suitable for use.
I’m sorry to hear about the situation you're facing. Here's some insight that might help with the electrical aspect:
1. Safety Certificate with an Old Fuse Box:
An old fuse box, while outdated, doesn’t automatically mean the electrics are unsafe. An electrician could issue an Electrical Installation Condition Report (EICR), which assesses the safety of the system. However, an old fuse box may not meet current standards (such as the requirement for Residual Current Devices, or RCDs), and this could result in a lower rating. If the wiring and other components are sound, it may be possible to get a satisfactory report, though the recommendation would likely still be to upgrade the fuse box.
2. New Fuse Box without Rewiring:
In many cases, it's possible to upgrade the fuse box (also called a consumer unit) without needing a full rewire. An electrician could inspect the current wiring and confirm if it’s in good condition. If the wiring is intact, they may only recommend upgrading the consumer unit, which is significantly cheaper than rewiring the entire property.
The cost of upgrading a fuse box can vary, but typically it ranges between £300 and £600 in the UK, depending on the complexity of the job and the region. It’s much less expensive than a full rewire.
3. Perception in the Report:
Since the report might cause concerns for potential buyers, you could consider getting a second opinion from another electrician or a more detailed report explaining that the wiring is safe and compliant, except for the outdated fuse box. If you get an electrician to provide an updated consumer unit, it can help alleviate concerns and improve the score on future reports.
4. Next Steps:
Consult with an Electrician: Have a licensed electrician inspect the property to determine whether the wiring is still safe and to provide an estimate for upgrading the fuse box.
Report of Assurance: Ask for a detailed EICR that can provide reassurance to buyers, especially if the only issue is the fuse box.
Negotiate: If funds are tight, you might negotiate with potential buyers to share the cost of the upgrade.
By upgrading the fuse box, you’ll likely remove a lot of concerns from buyers, and if no rewire is needed, it could make the property more attractive without a massive expense.
If you have an old fuse box you will also have old wiring. Essentially there is nothing 'unsafe' with old installations - they will comply to the regulations around at their time of installation. However, old wiring will have been used and will over time wear out just like anything else, the main problem being in the breakdown of insulation. New fuse boxes have switches that are extremely sensitive and if there is a breakdown these switches will not accept the wiring, meaning it cannot be done or causing nuisance tripping. Another problem with old wiring is that electrical screws can become lose, causing wires to become loose, causing unsafe situations. On the flipside, if the wiring is ok, and you have earthing to water stopcock and gas, you will only make it safer by upgrading the fuse box.
Hope this is of some help to you.
Cheers
Will
Power Electrical
There are minimum requirements that must be met
But its also at each electricians discretion as they make want more upgraded to put there name to it
The condition of the cable is determined after test, let your electrician carry out the continuity test, insulation resistance test and other necessary tests, then advise on minimum work required to bring to a safe condition for sale, not necessarily a new fuse system.
Hi, we could send an electrician to site to inspect the current condition of the fuse box, we would recommend updating it for a new one that and provide a free quote for that. Regards to the rewiring, if the electrician believes it would be fine with a new fuse box then we can issue the relevant certificates, otherwise we can provide a separate quote for that work too.
I would recommend getting an electrical test on all the circuits if they all pass then you will just need to update the fuse board with the exciting wires and circuits. If some faults accur on circuits you will need to get these rectified before having the new board fitted. But you do not always need a rewire you can just update a fuse board if everything tests ok.
Get a eicr report completed to acquire whether the electrics meet the bs7671 regulations prior to upgrading the consumer unit.
An EICR (electrical installation condition report) could be done on the properties electrical installation.
That being said, there is no guarantee that the property owner would get a satisfactory report, and COULD highlight problems that would need rectifying IMMEDIATELY.
Firstly a plastic fuse box is a c3 (recommended remedial action) not mandatory. If the wiring is showing low insulation resistance reading, then a rewire may be needed, but if all readings are OK, you have protection at ccu (RCDs or RCBOs) and there is no c1 (Danger present) or c2 (potentially dangerous) then a satisfactory certificate can be provided. If you have no protection at fusebox weather its old or not a satisfactory certificate cant be provided. Ideally a whole rewire would be better but can be costly. If financially possible upgrade ccu and that will get you a satisfactory certificate and also help in the selling of the house.